Defective Summary
Roof
1. East Chimney Chimney:
Brick: Mortar on chimney is deteriorated. Recommend further
evaluation and repair by a qualified contractor.
Electrical
2. Basement Electric Panel Breakers:
Copper and Aluminum: Label all circuits.
3. Basement Electric Panel Is the panel bonded?
No Service panel is not bonded. Recommend further
evaluation by a licensed electrical contractor.
Plumbing
4. Basement Water Heater Flue Pipe:
Single Wall: Flue pipe is not properly secured together
with screws, requires repair. Current building standards require single wall pipe
have a minimum of 6" of clearance from all combustible material. Not present in
basement, requires repair.
Air Conditioning
5. East Side of House AC System A/C System Operation:
Functional at time of inspection: Improper
temperature differential. Recommend further evaluation by a qualified HVAC
technician.
Heating System
6. Basement Heating System Heat Exchanger:
6 Burner: Loose screw present in heat exchanger,
requires removal.
7. Basement Heating System Blower Fan/Filter:
Direct drive with reusable filter: Safety
disconnect inoperable at furnace fan compartment, recommend repair.
8. Basement Heating System Flue Pipe:
Double Wall: Current building standards require double
wall flue pipe have a minimum of 1" clearance from combustible materials. Not
present in attic, recommend repair.
Structure
9. Foundation:
Concrete: Cracks with evidence of seepage present at south wall in
basement. Cracks with evidence of seepage present at north and east walls in
crawlspace. Recommend further evaluation and repair by a qualified contractor.
Attic
10. Main Attic Roof Framing:
2x4 Truss: Truss is damaged at center of west facing roof
surface. Recommend further evaluation and repair by a qualified contractor.
11. Main Attic Sheathing:
Plywood: Staining present at multiple locations. Potential
microbial growth, recommend testing and remediation per EPA guidelines.
12. Main Attic Ventilation:
Roof and soffit vents: Ends of truss bays are blocked with
insulation, recommend installing baffles to allow proper ventilation. Roof vent is
obstructed by insulation, recommend repair.
Basement
13. Main Basement Basement Stairs/Railings:
Wood stairs with wood handrails: Spindle spacing is
greater than 4" and not in compliance with current building standards.
Bathroom
14. 2nd floor hall Bathroom Ceiling:
Painted Drywall: Water damage present near north wall, dry
at time of inspection. Recommend repair and monitor for leaks.
15. 2nd floor hall Bathroom Electrical:
110 VAC outlets and lighting circuits: Current building
standards require all bathroom outlets be GFCI protected.
16. Master Bathroom Electrical:
110 VAC outlets and lighting circuits: Current building
standards require all bathroom outlets be GFCI protected.
17. Master Bathroom Shower/Surround:
Fiberglass pan and tile surround: Loose and missing
grout at south wall, requires repair.
18. 1st floor 1/2 Bath Half Bathroom Electrical:
110 VAC outlets and lighting circuits: Current
building standards require all bathroom outlets be GFCI protected.
Bedroom
19. 2nd Floor West Bedroom Electrical:
110 VAC outlets and lighting circuits: Closet light
requires covered lens.
20. 2nd Floor Southwest Bedroom Electrical:
110 VAC outlets and lighting circuits: Closet light
requires covered lens.
21. 2nd Floor Southeast Bedroom Electrical:
110 VAC outlets and lighting circuits: Closet light
requires covered lens.
22. Carbon Monoxide detectors present
No Illinois state law requires carbon monoxide detectors
within 15' of every sleeping room.
Living Space
23. Dining Room Living Space Ceiling:
Painted Drywall: Water damage present at east wall, dry at
time of inspection. Recommend repair and monitor for leaks.
Kitchen
24. 1st Floor Kitchen Dishwasher:
Electrolux: Dishwasher drain tube is improperly installed at
disposal, recommend repair by a qualified contractor.
25. 1st Floor Kitchen Electrical:
110 VAC outlets and lighting circuits: Current building
standards require all kitchen counter outlets be GFCI protected.
Laundry Room/Area
26. 1st Floor Laundry Room/Area Washer and Dryer Electrical:
110 VAC: Current building standards
require all outlets within 6' of a water source be GFCI protected.
Fireplace/Wood Stove
27. Family Room Fireplace Fire Box
Brick: Loose and missing mortar in fire box, recommend
repair.