地线 与 零线, 我google 最好的答案

来源: PtLandlord 2020-11-17 19:17:34 [] [旧帖] [给我悄悄话] 本文已被阅读: 次 (607 bytes)

The neutral and ground bus should not be connected (bonded) in the sub panel.

If there is a service disconnect outside, then everything downstream (including your distribution panel) is now considered a sub panel. The only place the neutral and ground can be together is at the service panel (your disconnect outside). The neutral and ground must be isoloated (floating) in a sub panel.

所有跟帖: 

太对了,service panel 和 sub panel 就像父子,都是男人,责任不一样。 -上海大男人- 给 上海大男人 发送悄悄话 上海大男人 的博客首页 (0 bytes) () 11/17/2020 postreply 21:01:21

At the main panel, the neutral and the ground are together -orlandomagic- 给 orlandomagic 发送悄悄话 orlandomagic 的博客首页 (0 bytes) () 11/18/2020 postreply 05:23:08