因此换board 不解决问题很正常。here is what you need to do:
1)check if you have 24v between R and C. Voltage=0,?bad transformer; v=24, go to next
2)at the board, put a jump wire between R and Y (connect R & Y), condenser should be on since you have a new contactor. If not, bad wire between board and contactor.
3)jump R and G, blower should be on.
4)If 2) and 3) both are working, the problem is your thermostat or wire between the board and thermostat.
问题出在低压(24V)电路。cooling is not controled by the board. it iis by t